How do you fix counter battens on to wood fibre sarking boards?

 
Chris Brookman
(@chris)
Member Admin
Counter-battens would be fixed through the wood fibre sarking boards with long screws and require at least 40mm penetration into the timber. Also, on steeper pitches the screws can be installed at alternate angles to improve the sheer resistance of the battens. Please see the diagram here -  https://www.backtoearth.co.uk/wp-content/uploads/2021/02/8.07_Sarking-board-detail_ENG.pdf

Hope that helps

Quote
Topic starter Posted : 10/02/2021 11:35 am
Tony Hickinbottom
(@tony-hickinbottom)
Member

According to BS 5534, 'the nails used to fix battens to rafters should usually have a diameter of at least 3.35mm. The nails should provide a minimum of 40mm penetration into the rafter, so a nail length of 65mm is generally recommended'. Obviously this requirement is achieved, for the counter battens, using the method you suggest Chris. However my question is if we try to comply with BS 5534 the batten nails fixing the slate batten to the counter batten will penetrate both battens through the membrane and into the wood fibre sarking board by 15mm. Apart from the hundreds of puncture holes in the membrane the end 15mm of the batten nail will only be in wood fibre sarking board and therefore offers no pull out resistance. Is this a problem? if so whats the solution?   

I would welcome anyone's thoughts

Tony

ReplyQuote
Posted : 24/06/2022 6:53 am
Chris Brookman
(@chris)
Member Admin

Hi Tony

Thanks for your message. We would usually suggest using screws to hold the counter battens on and they need to penetrate the rafters by 40mm as a minimum. You'd therefore need to accommodate the thickness of the batten and the insulation to achieve this.

In terms of punctures, we do have nail sealing tape that can be used to properly seal under the battens but generally the compression of the batten against the surface of the wood fibre boards is enough to seal it from water tracking sideways under the counter-battens and through the breathable membrane.

Hope that helps.

ReplyQuote
Topic starter Posted : 07/07/2022 10:54 am
Chris Brookman
(@chris)
Member Admin

Hi Tony

Yes, the slate batten nails may puncture the membrane but as any punctures will be under the counter-battens this is not a problem. The nails that hold the slates are much shorter and barely protrude from the underside of the battens.

I would still recommend using the breathable membrane over the wood fibre board as an additional layer of protection and also to appease Building Control, who tend not to understand a construction without it.

ReplyQuote
Topic starter Posted : 26/07/2022 1:40 pm
Share:

CPD Training

We offer CPD training for architects practices across Devon and Cornwall.

Software Modelling

We offer dynamic heat and moisture modelling as well as condensation risk analyses.

Building Plan Review

If you have some plans and would like our opinion on which materials would be the best for you, contact us.

Overview

Back to Earth is a natural building material supplier. We're not your typical builders'​ merchant though and instead work closely with our clients during the planning, designing and building phases of projects.

Back to Earth is a proud signatory of the Anti-Greenwash Charter:

© 2018 Back to Earth